250.62 Grounding Electrode Conductor Material. The
grounding electrode conductor shall be of copper, aluminum,
or copper-clad aluminum. The material selected shall
be resistant to any corrosive condition existing at the installation
or shall be protected against corrosion. The conductor
shall be solid or stranded, insulated, covered, or bare.
Yeah I mean really what negative effect could using an insulated conductor have?Obviously you need a bare copper if you use #4 as a cee but not to the ground rod. The inspector needs to actually think about it for a second.... I always use bare copper but not because insulated isn't allowed...
Unless it was insulated AT the ground rod under the clamp... Would hope even the most junior electrician would not make that mistake.
I have and if you use the right size monofilimant you're fine.I take it you have never seen someone bond plastic water pipe. LOL