I am looking for some clear(ish) guidance on acceptable levels of insulation damage on a few types of conductor; XHHW-2, THHN-2 and 2kV PV Wire. I inspect electrical systems and come across varying levels of conductor insulation damage. This is everything from very minor cosmetic nicks all the way to exposed conductor. The area I am continually having issue with is understanding the middle ground and where visible damage is too much. I have see conductor max out an insulation resistance test, yet have serious visible damage albeit without exposing metal.
I find myself in a position of horse trading acceptable levels of damage with electricians and default to a 'no damage is acceptable' position. I am an Owner's Rep, and need to provide quality, but I don't want to be punitive and unreasonable.
My company specifies XHHW-2 frequently. An electrician pointed out that it has a 'soft' insulation that shows minor impacts readily and then prefer alternatives such as THHN-2.
Recently when discussing problem conductors, an electrician pointed me to UL44. There are several relevant sections, but for do not answer the question fully to my understanding.
UL44.
14.1The insulation shall not have any defects visible with normal or corrected vision without magnification.(I take this to mean from the manufacture)
14.2 Any repair or joint in the insulation shall be made in a workmanlike manner resulting in all parts affected in the process complying with the same electrical tests as the remainder of the insulation. The thickness of insulation at the repaired part or joint shall comply with the requirements in 15.1.1.
15.1.1 states that there are average and minimum insulation thicknesses per Tables 15.1-15.6
So I have a couple questions:
What are Standards speak to insulation damage?
What damage is acceptable if any?
If a repair is acceptable, how many repairs to a single conductor are acceptable?
Scenario1: Conductor is pulled, IRT is performed and the value exceeds the minimum or maxes the tester. Damage beyond reasonable cosmetic is noted. Is the conductor acceptable?
Scenario2: Conductor is pulled, IRT is performed and the value exceeds the minimum or maxes the tester. Damage beyond reasonable cosmetic is noted, but the minimum insulation value of Table 15.3 is present. Is the conductor acceptable?
Many thanks.
I find myself in a position of horse trading acceptable levels of damage with electricians and default to a 'no damage is acceptable' position. I am an Owner's Rep, and need to provide quality, but I don't want to be punitive and unreasonable.
My company specifies XHHW-2 frequently. An electrician pointed out that it has a 'soft' insulation that shows minor impacts readily and then prefer alternatives such as THHN-2.
Recently when discussing problem conductors, an electrician pointed me to UL44. There are several relevant sections, but for do not answer the question fully to my understanding.
UL44.
14.1The insulation shall not have any defects visible with normal or corrected vision without magnification.(I take this to mean from the manufacture)
14.2 Any repair or joint in the insulation shall be made in a workmanlike manner resulting in all parts affected in the process complying with the same electrical tests as the remainder of the insulation. The thickness of insulation at the repaired part or joint shall comply with the requirements in 15.1.1.
15.1.1 states that there are average and minimum insulation thicknesses per Tables 15.1-15.6
So I have a couple questions:
What are Standards speak to insulation damage?
What damage is acceptable if any?
If a repair is acceptable, how many repairs to a single conductor are acceptable?
Scenario1: Conductor is pulled, IRT is performed and the value exceeds the minimum or maxes the tester. Damage beyond reasonable cosmetic is noted. Is the conductor acceptable?
Scenario2: Conductor is pulled, IRT is performed and the value exceeds the minimum or maxes the tester. Damage beyond reasonable cosmetic is noted, but the minimum insulation value of Table 15.3 is present. Is the conductor acceptable?
Many thanks.