retire09

Senior Member
Do you know what the insulation type is for the individual conductors inside NM cable?
I thought it used to be stamped on the cable or the box as THHN and THWN.
Was I dreaming?
Was that true?
Has that changed?
 

bphgravity

Senior Member
Location
Florida
I do not have my UL marking guides in front of me at this moment however I believe NM cable is only required to have insulated conductors with a 90?F rating as identified in Table 310.13 and be marked as "NM-B". See 334.112 of the NEC.
 

Rockyd

Senior Member
Location
Nevada
Occupation
Retired after 40 years as an electrician.
nm-b cable has thhn insulated conductors

Thank you, if this is the case, then that explains why romex is can't be in a wet location!
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
barbeer,
nm-b cable has thhn insulated conductors
Can you cite a document that says this? There are no markings on the conductors and the UL standard only requires the use of 90C conductors without specifiying the type. I agree that they appear to be THHN.
Don
 

bphgravity

Senior Member
Location
Florida
Unless you are just trying to satisfy curiosity, it doesn't really matter what the individual conductors are insulated with. The cable is an assembly and the individual conductors cannot be used without its sheathing.

I constantly find NM installations in outdoor raceways, and upon re-inspect I find the installer simply withdrew the conductors from the sheathing and reused them. Once they are withdrawn they are useless, unless you plan on stripping the insulation and using them as equipment grounds?
 

barbeer

Senior Member
Don.......

Such a wealth of info the internet is! Check out:

http://appprod.southwire.com/Produc...dyPage=/tab_prodcat.jsp&label=Product Catalog

http://appprod.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet6

These two links are for southwire, I am sure there are others. You are what I can see correct about the non thhn insulation. The conductors are rated for 90 deg. Celcius though....but, if I read right they say to use the 60 deg. C column? A little confusung.

The hyperlink thingy is not working right? WEll......Maybe it is?
 
Last edited:

stickboy1375

Senior Member
Location
Litchfield, CT
bphgravity said:
Unless you are just trying to satisfy curiosity, it doesn't really matter what the individual conductors are insulated with. The cable is an assembly and the individual conductors cannot be used without its sheathing.]


How do I meet 6" of free wire in a box then?
 

bphgravity

Senior Member
Location
Florida
stickboy1375 said:
How do I meet 6" of free wire in a box then?

When you make a joke on the Forum, its best to indicate it's a joke or add a funny little face at the end of the joke. Otherwise, people may think you are actually being serious...
 

bphgravity

Senior Member
Location
Florida
Oh, I'm sorry. I thought your comment was pretty funny...

Obviously, the context of my post was in regard to conductors withdrawn from the cable assembly and used as individual conductors in a raceway or other wiring method. I think you would agree this procedure would not be code compliant, whereas the free conductors of a cable assembly exposed within an enclosure or box would be completely acceptable.

I am truly soory for you confusion...
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
stickboy1375 said:
I was kidding, but seriously if that conductor is thhn/thwn, then why a problem with removing the sheath? The only problem I see is the romex is not labeled....


That is the problem. You may be able to use the wire from inside of a piece of MC cable since some manufacturers use conductors that are labeled.
 

allenwayne

Senior Member
stickboy1375 said:
I was kidding, but seriously if that conductor is thhn/thwn, then why a problem with removing the sheath? The only problem I see is the romex is not labeled....

Not much different from using the conductors from a leftover piece of SER for a service.They have no markings so they can`t be used.
 

RampyElectric

Member
Location
Liberty SC
I read on a manufacturers website that they used THHN in their NM-B product. The fact of the matter is it could be any insulation, but since the wires arent marked/labeled, they might as well be pink elephants outside their sheathing. As for the original question, was it EVER labeled inside NM cable....no clue. Although, I have purchased MC recently and it was marked THHN. Be careful with bph, he is rarely incorrect. Trust me
 

JohnJ0906

Senior Member
Location
Baltimore, MD
As I read and understand it, it means the conductors inside the romex cannot be used by themselves because they are not indiviually marked. If they were individually marked, then, IMO, they could be used without the jacket.
 