Hello All,
Quick clarification on standards of insulation resistance testing.
I like to do megger testing of conductors as per IEEE/ANSI ATS 2013 which says that for cables rated 600V and above to test at 1000VDC for 1 min. They also give a table to say what the minimum acceptable value is for the insulation resistance test. For example, equipment rated 600V - 1000V the minimum rated insulation resistance value is listed to be 100MOhms. However, it does list an associated distance for the acceptable value. If I test a conductor that it 10 feet long versus one that is 1000feet long the one that is 1000ft long will naturally have a higher capacitance and therefore lower insulation resistance.
IEEE 525 (Guide for the Design and Installation of Cable Systems in Substations) and IEEE 422 (Guide for the Design and Installation of Cables Systems in Power Generating Stations)attempt to quantify the effects of distance in a formula for the minimum acceptable insulation resistance. The formula is: R(in MOhms) = (rated voltage in KV + 1) *1000/(length in feet).
I do not see why NETA ATS does not have a metric to adjust the minimum insulation value for distance of conductor, and I do not want to quote substation standards in my findings of insulation resistance results of long runs. What is everyone's experience in these situations?
Quick clarification on standards of insulation resistance testing.
I like to do megger testing of conductors as per IEEE/ANSI ATS 2013 which says that for cables rated 600V and above to test at 1000VDC for 1 min. They also give a table to say what the minimum acceptable value is for the insulation resistance test. For example, equipment rated 600V - 1000V the minimum rated insulation resistance value is listed to be 100MOhms. However, it does list an associated distance for the acceptable value. If I test a conductor that it 10 feet long versus one that is 1000feet long the one that is 1000ft long will naturally have a higher capacitance and therefore lower insulation resistance.
IEEE 525 (Guide for the Design and Installation of Cable Systems in Substations) and IEEE 422 (Guide for the Design and Installation of Cables Systems in Power Generating Stations)attempt to quantify the effects of distance in a formula for the minimum acceptable insulation resistance. The formula is: R(in MOhms) = (rated voltage in KV + 1) *1000/(length in feet).
I do not see why NETA ATS does not have a metric to adjust the minimum insulation value for distance of conductor, and I do not want to quote substation standards in my findings of insulation resistance results of long runs. What is everyone's experience in these situations?