Re: Insulation Resistance of Electrical Cable
If you can try obtaining the Dielectric Absorption Ratio (DAR). An example of a DAR is Meg reading at 60 sec/ meg reading at 30 sec. The following table was obtained from Recommended Practice for Electrical Equipment Maintenance, NFPA 70B, 2002 edition. The table serves as a guide to interpreting DAR ratios.
Table 1: Dielectric Absorption Ratio Testing:
Condition DAR
Poor < 1.1
Questionable 1.1 ? 1.25
Fair 1.25 ? 1.4
Good 1.4 ? 1.6
Excellent > 1.6
DAR tests are preferable because they are a ratio of changing resistance over time and are not subject to cable lengths. The Megohm value will be inversely proportional to the volume of insulation. Therefore a cable of 1000 ft length should have half the insulation resistance of a cable of 500 ft.
I was looking through NFPA 70B and I don't see a rule of thumb for "spot" megging. Hope this helps.
I see rules of thumb for motors but not cable.