We are doing a 480V insulation resistance test at 1000Vdc. Does anyone know what are acceptable values for resistance? Also what is the difference between a megger test and an IR test? thank-you
Does anyone know what are acceptable values for resistance?
oh, we are simply testing the cables for a three phase 480v, 30A circuit that feeds light pole
In general, you are looking for a really big number.
More specifically, you can calculate the expected value using the following equation:
IR = k * log(D/d)
where k is an insulation resistance constant that depends on the type of insulation you have, D is the diameter of the cable over the insulation, and d is the diameter of the cable under the insulation.
HOWEVER, the value you get from this equation will only be valid for 1000 feet of cable at 60 degrees F. If your situation is different from that (and it most likely is), then you will need to apply some scaling factors to get the right number. Even then, if the cable is dirty or the humidity where you are is high or you do something wrong, you'll get the wrong answer.
Perhaps you should consider having a qualified professional testing agency/individual do these tests for you...?
Excellent points. (I thought that equation was based on 68 Degrees F??)
Thank you.
I was using the 2006 'A Stitch in Time' as my reference for the temperature baseline. They say that rotating equipment and transformers are 68 degrees F but cable is 60 degrees F. That is on page 22, in the paragraph above the table and in the fine print below the table.
As for the equation, I don't have that textbook with me at the moment and I can't remember what it said about temperature, so I'll have to look it up later.Thanks for pointing it out either way. I don't want to be spouting stuff that I'm not sure is correct.
![]()
"A stich in time" seems to contridict it self (Look at page 20), I think that correction table on page 21 is just an example. ANSI?NETA specs say to correct inductive equipment to 40C and everything else to 20C.