Hello, I recently Purchased a Fluke 1587FC for a job I posted on this site. Next day I got a call for a blown fuse on L2 in the service disconnect. I don't believe it was overloaded since it serves only lights, and L1 only reads 40 amps on a 100 amp fuse.
The equipment and wire are about 75 years old. Wires are ran in RMC, 3 wire circuit, RMC is EGC
I disconnect all wires to test them
I did a spot test at multiple ranges ohm range from L2-G. Was fine till I got to 500v and 1000v. So I did a DAR test( the 30/60) and on L2 to ground. I got 328m to 585m. Dividing them gave me 1.1 so that wire looks like it's on its last leg (To me)
L1 to ground was 2.2g
L1 to N was 2.2g
Neutral to ground was 1.1g to 2g
L2 to L1 was 1.9g to 2g
L2-N was 1.5g to 2g
So looks like its Going to the RMC
I took a few classes on flux for insulating testing. So I feel I am correct. I would just like your guys input, since this is my First Insulation test by my self.
The equipment and wire are about 75 years old. Wires are ran in RMC, 3 wire circuit, RMC is EGC
I disconnect all wires to test them
I did a spot test at multiple ranges ohm range from L2-G. Was fine till I got to 500v and 1000v. So I did a DAR test( the 30/60) and on L2 to ground. I got 328m to 585m. Dividing them gave me 1.1 so that wire looks like it's on its last leg (To me)
L1 to ground was 2.2g
L1 to N was 2.2g
Neutral to ground was 1.1g to 2g
L2 to L1 was 1.9g to 2g
L2-N was 1.5g to 2g
So looks like its Going to the RMC
I took a few classes on flux for insulating testing. So I feel I am correct. I would just like your guys input, since this is my First Insulation test by my self.
Last edited: