Insulation testers.

Status
Not open for further replies.

knoppdude

Senior Member
Location
Sacramento,ca
Does anyone have experience using Simpsons 1000v insulation tester, and what is your opinion of it? I am looking to buy one of these, or the greenlee hand crank model. Any advice is appreciated.
 

knoppdude

Senior Member
Location
Sacramento,ca
Thanks Zog, the voltages would be 250-1000, and the tester would be used at least once daily, testing 480 volt motor branch circuits. What would you recommend as a better tester than these two?
 

zog

Senior Member
Location
Charlotte, NC
Thanks Zog, the voltages would be 250-1000, and the tester would be used at least once daily, testing 480 volt motor branch circuits. What would you recommend as a better tester than these two?

I can't remember the last 1000V megger I bought, but if you are doing motor testing you will want one that does DAR and PI tests for you. You don't want to hand crank a megger for 10 minutes :-(

A lot of LV guys seem to like the Fluke 1507 for basic testing. AEMC and Megger make quality units too. It is all about the features and ranges, for a 1000V you only need one that gets up into maybe 10 or more Gigohms.
 

knoppdude

Senior Member
Location
Sacramento,ca
Hi Zog,
I have been looking at what Megger has, and will talk with their local representative on tuesday. I have been using a hand crank AEMC, but it is malfunctioning, and needs repair. It did reveal several problems while it worked, so it payed for itself in that regard. Megger makes a 250,600,1000v device that is battery powered, and an analog indicator. I can't recall the model number, but will tell the rep what I am using it for, and what he recommends. I know they are not cheap, but I have had three of the hand crank types fail in the last 4 years, plus you do have to keep turning for several minutes in some cases. At the risk of sounding stupid, what is DAR and PI testing? Thanks again for the advice.
 

brian john

Senior Member
Location
Leesburg, VA
The lastly I bought 4- megger 1000 VDC all were JUNK, within 18 months all 4 were in the trash. Now this was a while ago, and I am sure they have improved. But I wasted $3,200.00 and I will not give them a more dime. I have other issues with megger and their service. IMO just not the quality company they once were.

Fluke seems to be the current work horse in the industry for day to day use.
 

zog

Senior Member
Location
Charlotte, NC
, what is DAR and PI testing?

When you megger something you are not really measuring resistance, you are measuring current (And calculating resistance) There are 3 currents being measured (Important to understand you are measuring current, no such thing as an ohmeter) this is very important to understand when testing inductive equipment.

(View attachment before reading on) 3 currents.jpg

When a high DC voltage is first applied the total current (a) consists of three current components;

1. Leakage current
2. Capacitance charging current
3. Absorption current

Conduction/Leakage Current (b) - This current passes through the surface of the insulation. The magnitude of current flow depends on the resistance of the insulation. Surface leakage is usually not a problem because it can be eliminated through external cleaning.

Capacitive Current (c) - The insulating specimen appears, ideally, as a capacitor. As a DC voltage is applied to a capacitor initial charging current flows until the voltage drop across the component equals the source voltage. As the capacitor charges, its charging current decreases to a minimum. This is called its steady-state value.

Dielectric Absorption Current (d) - This current also appears at the initial application of test voltage the same as capacitance current. This current is required to polarize the insulating medium. In other words it is energy absorbed by the insulating system.

To seperate these different qualities of an insulating system you can use the time they take to decay (As you can see on the attachment). Since the currents are decaying the indicated resistance reading on your display will go higher.

When you test, record the values at 30 seconds, 1 minute, and 10 minutes. The 1 mniute reading divided by the 30 second reading is called your Dielectric Absorbtion Ratio (DAR). The 10 minute reading divided by the 1 minute reading is your Polarization Index (PI). The values of these ratios can be used to determine the condition of the entire insulating system and allow you to do a condition assement of your assets.

Understanding these qualities is important, I have seen many people meg a motor for a few seconds and say it is good, they just did not know what they were reading.

Another key thing is properly correcting your readings for temature. Most equipment is corrected to 20C, motors and generators usually to 40C. Temp makes a huge difference!!
 

knoppdude

Senior Member
Location
Sacramento,ca
Thank you for the replies. Brian John, Fluke does seem to be the best choice, and they sell devices that can be used to determine the Polarization Index, and DAR. Plus they seem to have a more available supplier network, and the price is not overwhelming. Zog, you have opened up a whole new world of insulation testing for me. I can't quite make out the jpeg, but have found some information on the internet. I really had no idea about insulation testing, and usually only caught existing insulation failures, either motors or branch circuits. Now I see that the condition of insulation can be measured over time, and deterioration rates determined. I feel like I just found a thousand dollars in the attic.
 

zog

Senior Member
Location
Charlotte, NC
Thank you for the replies. Brian John, Fluke does seem to be the best choice, and they sell devices that can be used to determine the Polarization Index, and DAR. Plus they seem to have a more available supplier network, and the price is not overwhelming. Zog, you have opened up a whole new world of insulation testing for me. I can't quite make out the jpeg, but have found some information on the internet. I really had no idea about insulation testing, and usually only caught existing insulation failures, either motors or branch circuits. Now I see that the condition of insulation can be measured over time, and deterioration rates determined. I feel like I just found a thousand dollars in the attic.

Download "A stitch in time" from the Megger website, it is a very good introduction to IR testing.
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
When you megger something you are not really measuring resistance, you are measuring current (And calculating resistance) There are 3 currents being measured (Important to understand you are measuring current, no such thing as an ohmeter) this is very important to understand when testing inductive equipment.

(View attachment before reading on) View attachment 5482

When a high DC voltage is first applied the total current (a) consists of three current components;

1. Leakage current
2. Capacitance charging current
3. Absorption current

Conduction/Leakage Current (b) - This current passes through the surface of the insulation. The magnitude of current flow depends on the resistance of the insulation. Surface leakage is usually not a problem because it can be eliminated through external cleaning.

Capacitive Current (c) - The insulating specimen appears, ideally, as a capacitor. As a DC voltage is applied to a capacitor initial charging current flows until the voltage drop across the component equals the source voltage. As the capacitor charges, its charging current decreases to a minimum. This is called its steady-state value.

Dielectric Absorption Current (d) - This current also appears at the initial application of test voltage the same as capacitance current. This current is required to polarize the insulating medium. In other words it is energy absorbed by the insulating system.

To seperate these different qualities of an insulating system you can use the time they take to decay (As you can see on the attachment). Since the currents are decaying the indicated resistance reading on your display will go higher.

When you test, record the values at 30 seconds, 1 minute, and 10 minutes. The 1 mniute reading divided by the 30 second reading is called your Dielectric Absorbtion Ratio (DAR). The 10 minute reading divided by the 1 minute reading is your Polarization Index (PI). The values of these ratios can be used to determine the condition of the entire insulating system and allow you to do a condition assement of your assets.

Understanding these qualities is important, I have seen many people meg a motor for a few seconds and say it is good, they just did not know what they were reading.

Another key thing is properly correcting your readings for temature. Most equipment is corrected to 20C, motors and generators usually to 40C. Temp makes a huge difference!!

Thanks Gar,

Most people think megohmmeters are just sensitive DVOMs and don't really know how to use them.

For troubleshooting I have found that my 200M setting on my DVOM is sufficient to locate problems, even with locating ground faulted devices. A Megger is great for confirmation, but one has to be careful about what one put 500 volts to.
 

wptski

Senior Member
Location
Warren, MI
Most PI/DAR tests using a Fluke 1507 will result in an "Out of Range" error because it lacks the needed maximum range for those tests. I'm not even sure if Fluke's 1550B model is any better for PI/DAR testing.
 

knoppdude

Senior Member
Location
Sacramento,ca
I just bought the Fluke 1507, and it seems satisfactory for what work I will be doing. I also printed out and am reading through "A stitch in time", free online, and very worth reading. It explains more about insulation testing than I ever understood. As this model has a 10 G Ohm range, it will read error if the insulation is in good shape on the PI and DAR tests. I called the Fluke people, and they said that all this means is just that, that the insulation is in very good shape, and outside the range of the meter to measure. So far I am happy with it, and found some problems in the motor branch circuits I tested, and confirmed that others were good. Found one 300HP crusher motor that was in such bad shape, that it caused the meter output voltage to drop during the test. I got such a low PI score that the breaker will probably trip on startup. Fortunately, it is temporarily out of service. Thanks for all of the responses.
 

zog

Senior Member
Location
Charlotte, NC
Glad to help, I think this stuff should be standard material for any electricial training program. It is a valuable tool and knowledge for T/S most anything.
 

wptski

Senior Member
Location
Warren, MI
I just bought the Fluke 1507, and it seems satisfactory for what work I will be doing. I also printed out and am reading through "A stitch in time", free online, and very worth reading. It explains more about insulation testing than I ever understood. As this model has a 10 G Ohm range, it will read error if the insulation is in good shape on the PI and DAR tests. I called the Fluke people, and they said that all this means is just that, that the insulation is in very good shape, and outside the range of the meter to measure. So far I am happy with it, and found some problems in the motor branch circuits I tested, and confirmed that others were good. Found one 300HP crusher motor that was in such bad shape, that it caused the meter output voltage to drop during the test. I got such a low PI score that the breaker will probably trip on startup. Fortunately, it is temporarily out of service. Thanks for all of the responses.
The point of PI/DAR tests is to track over time from new possibly, so if the 1507 won't run the test, what good is it? Sometimes the 1507 will run the test if 1000V which maybe be higher than required. There are other units like from AEMC that will run a PI/DAR test at 500V where a 1507 fails to even at 1000V. What does that have to say about the 1507's specs?

I suppose that one could chart the "Out of Range" error at max of the particular range your using.

I have conviced HVAC Techs planning to purchase a 1507 not to because their plans were to perform PI/DAR tests.
 

jimbo123

Senior Member
I have seen electricians use their crank meggers for about 20 seconds and determine its either good or bad motor or what ever they were checking.
Sounds like they were not testing correctly. Sounds like we got great tips.
 