I hope I'm in the right forum. I am working on a mitigation plan for a house fire where lightning was the initiating cause. The lightning struck a tree 20' from the front wall directly over a water line. The copper pipe was heated to such an extent that it ignited joists where it entered the house. Fourteen branch circuits were damaged by fire and heat attack. No arcing is apparent other than small beads on a couple conductors where arcing occurred through the fire damaged insulation.
The owner wants the whole house gutted and rewired because he believes lightning has compromised his cables. I tested all the circuits in the house with a Fluke 1587 at 500V. All but two circuits tested ">550 M". The owner wants documentation stating that this is acceptable. I know about the 1 megohm/1000V "rule of thumb" but that's not quite 'official' enough. Is there a standard that covers this?
Thank you very much for your help
Gig em Ags!
Txaggie84
The owner wants the whole house gutted and rewired because he believes lightning has compromised his cables. I tested all the circuits in the house with a Fluke 1587 at 500V. All but two circuits tested ">550 M". The owner wants documentation stating that this is acceptable. I know about the 1 megohm/1000V "rule of thumb" but that's not quite 'official' enough. Is there a standard that covers this?
Thank you very much for your help
Gig em Ags!
Txaggie84