The issue is the CTs can't be removed without disassembling the switchboard.
Will it be safe to do the DC megger test on the busbar while the secondary of the CT of the busbar is open circuited?
Hello,
When I do a 1000V insulation test on a LV switchboard, shall I disconnect the CTs or measuring devices from the test circuit?
Meggering the bus with the CTs in place has two problems. The first was already discussed in that you should ensure the CT secondary is short circuited. Second, 1000 Volt DC testing may leave the CT's polarized and may cause an operation immediately upon energizing. To avoid this, I suggest AC high potential testing where CTs are left in the circuit.
Hope this helps,
Newton Law
Yes, you are correct. But it has been our experience that the person starting the job may not be the one that finishes it and to avoid burnt up CTs the safest practice is to keep them shorted till the load wires are connected.Having CTs open circuited is only a concern when there is alternating current flowing through the primary. It would not matter during an insulation resistance test, just as long as the secondaries were reconnected prior to turning the gear back on.
Yeah, I don't see it either. The CTs are coupled to the power circuit via the expanding / contracting AC fields created by CURRENT flow in the circuit, they don't know or care what the voltage is, and even if there were some current flowing in the DC circuit, it would only expand ONCE. Your hi-pot tester likely has fuse protection at something like 2A, so not even that much current would flow and would barely even register on a CT.I do not see how DC voltage (and no current) applied to the conductor could "polarize" the CT wires or core to the point that they could cause a differential current on the secondary when the conductor is re-energized.