PhaseShift
Does anyone know where I can find good insulation testing standards / specifications for cable insulation and motors?
IEEE, NETA, NEMA, etc...?
Would the motor specs be in the NETA "ATS" 2009?
What is the difference between NETA standards for motor and IEE-43 standards?[/qupte]
IEEE 43 is one of the references noted and some of the motor testing info in NETA is drawn from that standard.
Depends on the type of motor, and needs to be temp corrected to 40 degrees C. If the windings are at room temp your IR values would need to be about twice that.For motor under 200hp you it states that an IR test result of 5meg is acceptable for motor built in 2005?