Grouch
- New York, NY
Hey guys,
I've come across this situation in a prior project, and I want to try to make sure there's no mistake.
In the attached pic you'll see the main feeder coming into the lugs of an MLO panel (the red and black wires). It's a 120/208 volt, single phase, three wire copper feeder. The feeder insulation has no print on it unfortunately. With a caliper I measured the diameter of each wire, and it matches with #8 AWG.
My question is, does the insulation look to be type TW, forcing me to use the 60 deg. C column of the ampacity table 310.15(B)(16)?
Or does it look to be something else, such as type THWN / THW / THHW or THHN, allowing me to use the 75 deg. C column, and therefore a higher amperage rating for the wire?
I'm afraid to use the higher ampacity rating in a load calculation. If the insulation happens to be TW, I have to use the lower ampacity rating for the wire.
Thanks for the help!