This is pretty senseless spec. I've never seen this. It usually tell you to use either or in specific situations.
It's basically telling you choose between THHN or XHHW, no?
2.02 CONDUCTORS AND CABLES
A. Conductors and cable for power, lighting, control and signal circuits shall have copper conductors of
not less than 98 percent conductivity and shall be insulated to 600V. All conductors shall be
stranded except where specifically noted otherwise, see 2.06 below.
B. Type of conductor and cable for the various applications shall be as follows:
1. Type THWN-2 or XHHW-2 (75 degrees C) shall be used for branch circuits, panel and
equipment feeders in wet and dry locations, including exterior site wiring.
2. Type THHN-2 or XHHW-2 (90 degrees C) shall be used for branch circuits, panel and
equipment feeders in dry locations only and used where lighting branch circuit conductors are
routed through fluorescent fixture channels
2.04 CONDUCTOR AND CABLE APPLICATIONS
A. Concealed Dry Interior Locations: Use only building wire in raceway, building wire with Type THHN-2/XHHW-2
insulation in raceway, or metal clad cable.
B. Exposed Dry Interior Locations: Use only building wire in raceway, building wire with Type THNN-2/XHHW-2
insulation in raceway.
C. Wet or Damp Interior Locations: Use only building wire with Type THWN-2/XHHW-2 insulation in
raceway.
D. Exterior Locations: Use only building wire with Type THWN-2/XHHW-2 insulation in raceway.
It's basically telling you choose between THHN or XHHW, no?
2.02 CONDUCTORS AND CABLES
A. Conductors and cable for power, lighting, control and signal circuits shall have copper conductors of
not less than 98 percent conductivity and shall be insulated to 600V. All conductors shall be
stranded except where specifically noted otherwise, see 2.06 below.
B. Type of conductor and cable for the various applications shall be as follows:
1. Type THWN-2 or XHHW-2 (75 degrees C) shall be used for branch circuits, panel and
equipment feeders in wet and dry locations, including exterior site wiring.
2. Type THHN-2 or XHHW-2 (90 degrees C) shall be used for branch circuits, panel and
equipment feeders in dry locations only and used where lighting branch circuit conductors are
routed through fluorescent fixture channels
2.04 CONDUCTOR AND CABLE APPLICATIONS
A. Concealed Dry Interior Locations: Use only building wire in raceway, building wire with Type THHN-2/XHHW-2
insulation in raceway, or metal clad cable.
B. Exposed Dry Interior Locations: Use only building wire in raceway, building wire with Type THNN-2/XHHW-2
insulation in raceway.
C. Wet or Damp Interior Locations: Use only building wire with Type THWN-2/XHHW-2 insulation in
raceway.
D. Exterior Locations: Use only building wire with Type THWN-2/XHHW-2 insulation in raceway.