interchanging motor satrt capacitors

Status
Not open for further replies.

markstg

Senior Member
Location
Big Easy
Can you substitute motor start capacitors with different uf/VAC combinations if you don't have an exact replacement?

On my outside AC compressor and fan, I did that to get them to start over a weekend. On Monday went and got the correct size. Voltage was a match though, just cap values were different.
 

Mgraw

Senior Member
Location
Opelousas, Louisiana
Occupation
Electrician
Can you substitute motor start capacitors with different uf/VAC combinations if you don't have an exact replacement?

If you are asking about a start capacitor (usually 70 mfd or higher) the voltage needs to be right but the mfd can be +/- 10 percent. If you are asking about a run capacitor( below 70 mfd) then the voltage can be higher but the mfd needs to be exact.
 