PVMatt
Member
- Location
- Jacksonville, Florida
Hi all,
I know I addressed this before. But I do have this discussion with our master electrician (no solar experience) and the inspector who failed us on final inspection because this issue.
The argument of our master electrician is, that the hazard of heat building up at OCPD occurs ONLY at the first OCPD connected to the inverter.
Therefore, he thinks that the 120% rule applies to the AC Combiner panel (if used) and not at the main service panel if we use a AC Combiner Panel. For example, 3 branches of 16 M250 (enphase) each landed at the Ac Combiner Panel with 3x 20 amp breakers (assuming the Ac Combiner Panel bus bar rating in at least 80 amp) and then connect this AC Combiner Panel with a min #6AWG to Main Service Panel (200 amp main breaker and 200 amp bus bar rating) by using a 60amp breaker, is oaky. He refers to Article 705.12.(D)(7).
I believe this is not up to code as the 60 amp breaker landed in the 200Amp Main Service Panel exceeds the 120% rule for interconnection. No matter if the AC Combiner Panel is rated correct and save.
We will have a meeting with local inspector (JEA) and I like to be able to know to what article we have to refer and if the above practice is up to code?
Could you please point me in the right direction here?
Your knowledge and time is highly appreciated J
Regards,
Matthias
I know I addressed this before. But I do have this discussion with our master electrician (no solar experience) and the inspector who failed us on final inspection because this issue.
The argument of our master electrician is, that the hazard of heat building up at OCPD occurs ONLY at the first OCPD connected to the inverter.
Therefore, he thinks that the 120% rule applies to the AC Combiner panel (if used) and not at the main service panel if we use a AC Combiner Panel. For example, 3 branches of 16 M250 (enphase) each landed at the Ac Combiner Panel with 3x 20 amp breakers (assuming the Ac Combiner Panel bus bar rating in at least 80 amp) and then connect this AC Combiner Panel with a min #6AWG to Main Service Panel (200 amp main breaker and 200 amp bus bar rating) by using a 60amp breaker, is oaky. He refers to Article 705.12.(D)(7).
I believe this is not up to code as the 60 amp breaker landed in the 200Amp Main Service Panel exceeds the 120% rule for interconnection. No matter if the AC Combiner Panel is rated correct and save.
We will have a meeting with local inspector (JEA) and I like to be able to know to what article we have to refer and if the above practice is up to code?
Could you please point me in the right direction here?
Your knowledge and time is highly appreciated J
Regards,
Matthias