So I get a call there's no 220 in the house, I open up the panel and check voltages
A phase to neutral 120
B phase to neutral 64
And nothing on one phase on the load side of main so the problem is two fold the nutreals we're all corroded so I suggest a panel swap ,
I swapped out the panel and still the same problem
I open up the meter pan and volatges are good from Poco 2 gang meter pan both meters ok
So I check votages with the meter in at the Jaws and get normal readings but when I go to the lug.i get the 64 volts
I've never seen that before I found it pretty strange that the voltage wasn't getting across to the lug must have been some serious corrosion on that jaw