So I get a call there's no 220 in the house, I open up the panel and check voltages

A phase to neutral 120
B phase to neutral 64
And nothing on one phase on the load side of main so the problem is two fold the nutreals we're all corroded so I suggest a panel swap ,

I swapped out the panel and still the same problem

I open up the meter pan and volatges are good from Poco 2 gang meter pan both meters ok

So I check votages with the meter in at the Jaws and get normal readings but when I go to the lug.i get the 64 volts


I've never seen that before I found it pretty strange that the voltage wasn't getting across to the lug must have been some serious corrosion on that jaw
009fa9a00d676594a6b92aeb26c45bb4.jpg
15d19a803a7655f18cc0ca3ad72ea48b.jpg


Sent from my SM-G965U using Tapatalk
 
No they needed it anyway the wanted to put a bigger one in for an upcoming addition

Sent from my SM-G965U using Tapatalk
 
I didn't open the meter until after the panel was done and we still had the issue it's scheduled for Friday

Sent from my SM-G965U using Tapatalk
 
So I get a call there's no 220 in the house, I open up the panel and check voltages

A phase to neutral 120
B phase to neutral 64
And nothing on one phase on the load side of main so the problem is two fold the neutrals we're all corroded so I suggest a panel swap ,

I swapped out the panel and still the same problem

OK, you open the panel and check form A phase to neutral and get 120V. You check from B phase to neutral and get 64V.

I assume this was on the line side of the breaker. You should check from A phase to B phase to see if you get 240V.

You would not have got the 240V and that should tell you there is a problem upstream.

Now you check the meter base and find the real problem. Get permit and get power disconnected and change out the meter base and if need/wanted change out panel.

Doesn't matter now but the problem could just as easily been a bad connection form the power company.

The only thing wrong with changing out the panel was expecting it to solve the problem. It looked bad and probably needed to go.
 
I knew the problem was up stream panel needed to be changed anyway yes, Friday is scheduled for meter swap

Sent from my SM-G965U using Tapatalk
 
I know we shouldn't do it but u only do it when I feel comfortable that panel had alot if room and wires where new

Sent from my SM-G965U using Tapatalk
 
you are allowed to yoink the meter for safety...then they come back and re-lock it. but if live works for you...sweet.
 
So... you swapped the panel hot, knowing it won't solve the issue. Then a few days later you're going to have the power shut down to replace the meter socket/pan.

Silly me. I would have done both when the power is off, sans the chance of experiencing the Big Blue Zot.
 
you are allowed to yoink the meter for safety...then they come back and re-lock it. but if live works for you...sweet.

You'll get slapped for that in a lot of places around here; they get upset if you cut their meter tag.
 
You can't take out the meter for any circumstances with out Edison and that would usually take about three months from the date of your request

Sent from my SM-G965U using Tapatalk
 
You can't take out the meter for any circumstances with out Edison and that would usually take about three months from the date of your request

Sent from my SM-G965U using Tapatalk

What location is that where there is a 3 months time frame for a repair? Sounds unreasonable to me.
 
That's NYC. So you have a service call and find that the customer needs a new meter pan. They only have one leg working. So what are you supposed to do- send an email to Con Ed and wait 3 months?? Here in Westchester (also Con Ed) we yoink first and answer questions later. What are they going to do, throw you in jail?

-Hal
 
Status
Not open for further replies.
Top