Robbie R
- North Georgia
- Electrical Engineering Manager
Our local inspector has turned down some VAV's located above lay-in ceilings due to clearance issues with the access panel on the side of the VAV units. His interpretation is that per NEC (2020) Section 110.26(A)(4), the working space in front of the VAV access control panel needs to be maintained per Table 110.26(A)(1). There is also a FPN in the NEC Handbook below section 110.26(A)(4) that reinforces this ruling.
Our argument against this was found in the wording of Section 110.26(A)(4): "while energized", but after hearing his side of the story, I believe the Inspector is correct in his interpretation. We just had a meeting with the VAV manufacturer to let them know and they were also surprised, but could see the Inspector's ruling as legit. In my almost 30 years of engineering design, I've never come across this. Moving forward, this will now require some heavy coordination effort between all disciplines (Mech, Elec, Plumbing) to ensure there is clear space in front of these access panels.
In addition, I believe this NEC Section is not very clear and could use improvements on the wording, scope and intent.
Has anyone else seen this type of ruling and if so, how did you approach it?