I inspected a residential 200amp main electrical panel with a 200a breaker as the disconnect fed directly from the meter.
The electricial separated all of the neutrals and equipment grounds to separate terminal bars. BUT, what he did was to place a bonding strap from the neutral bar to the panel and did not use one for the equipment grounds.
This made the equipment grounds and grounding electrode conductor isolated from the main panel.
It was as though he was setting up as a sub-panel and put the bonding jumper on the wrong terminal bar.
As a result, I failed the installation.
However, I have a question for everyone. If he moved the bonding strap/jumper from the neutral bar to the equipment ground terminal bar and set it up like a sub-panel would that be acceptable since it really is a main panel?
I am asking this to see if it is required to bond the neutral to the panel at the main panel/disconnect? The panel is fed from the meter base by 4/0 al SE cable.
Thoughts?
The electricial separated all of the neutrals and equipment grounds to separate terminal bars. BUT, what he did was to place a bonding strap from the neutral bar to the panel and did not use one for the equipment grounds.
This made the equipment grounds and grounding electrode conductor isolated from the main panel.
It was as though he was setting up as a sub-panel and put the bonding jumper on the wrong terminal bar.
As a result, I failed the installation.
However, I have a question for everyone. If he moved the bonding strap/jumper from the neutral bar to the equipment ground terminal bar and set it up like a sub-panel would that be acceptable since it really is a main panel?
I am asking this to see if it is required to bond the neutral to the panel at the main panel/disconnect? The panel is fed from the meter base by 4/0 al SE cable.
Thoughts?