electricalperson
Senior Member
- Location
- massachusetts
today i was measuring voltage of wire inside a box that is in the ground. i had 50 volts on the simpson 260 and 50 volts on the fluke 117 high impedance function. i use the loz function and it went down to .6volts. i clip the test leads of the 260 to the wires and put my wiggy in paralell and voltage goes away. i try to locate other junction boxes and i find one that was buried and completly filled with water splices under water
i trace the wires back and find the one i was measuring voltage too went to a time clock that i was not working on. the wire that had 50 volts went there and wasnt energized by the time clock.
i emptied the water out of the buried box and replaced all the splices with waterproof wirenuts rated for DB. i left the leaves and pine needles off of the top
i energized the circuit and the 50 volts went away. i came to the conclution that the wire was picking up voltage from the 120 volt circuit. all the splices in the hidden junction box were under water so the voltage went through the water.
does this sound correct or could it of been something else i overlooked?
i trace the wires back and find the one i was measuring voltage too went to a time clock that i was not working on. the wire that had 50 volts went there and wasnt energized by the time clock.
i emptied the water out of the buried box and replaced all the splices with waterproof wirenuts rated for DB. i left the leaves and pine needles off of the top
i energized the circuit and the 50 volts went away. i came to the conclution that the wire was picking up voltage from the 120 volt circuit. all the splices in the hidden junction box were under water so the voltage went through the water.
does this sound correct or could it of been something else i overlooked?