:grin: Yes you do count it twice, but it has nothing to do with the screws. The yoke is the strap that the device is mounted on. It counts as two in your box fill calculations because they needed a standard cubic volume that was an average of the actual volumes of your various receptacles, switches, GFIs, etc. Otherwise, every device would have to have it's volume printed on it, and there isn't much room to print anything else on them as it is.[/QU
I can accept that however the definition of a single receptacle does say 1 contact device on the yoke. If thats the definition then you would have no tabs to cut and that ends the argument of whether or not you could use a duplex recep.