Got to a customer last nite and the complaint was that there was a J box that was"glowing". This was at a local bar in the U district so I wasnt sure if the students had had a bit too much or what. Lo and behold they were correct. Both cover plate screws were glowing red. When I remarked to the customer that it appeared that there were some gounded conductors in the box he said well why didnt the circuit breaker trip then? That puzzled me as well as he led me way back to the main panel and viola! a 400 amp 42 space you guessed it FEDERAL PACIFIC dinosaur with all breakers neatly still latched. As this panel cover was not marked very well we located the circuit in question by trial and error (prior to touching anything) by swithching off individual circuits until the red glow stopped. Repaired a melted mess in the box with 2 reds completly gone and most of the spring on the neutral red burned away. nasty mess to say the least. Cost the customer a good bit to fix but heck of a lot less than a fire. Of course we now will probably get the panel replacement as well as the customer now knows he owns a never trip federal pacific panel.