It’s only connected to that removable panel by tie wire to prevent the rebar stub from rotating or folding over when concrete is pouredRegardless of what they are trying to achieve the way it's connected to a removable panel would be reason to turn it down
I agree, if this were to be an acceptable method for a UFER I would want to see the #4 CU attached to the encased rebar and stubbed outThe first issue I see is that you can't stub the rebar out of the dirt like that. It has to be protected from corrosion such as turning up out of concrete within a wall cavity.
I'm afraid we may have a bunch of "4 Hatters" that think this is just fine although that gear in the background would seem to preclude a 4 hatter in this case from inspecting this in our state.If that is just a hole dug to contain the re-bar and concrete, and is NOT a footer or foundation, I don't believe I would accept it as a CEE.
I do understand the NEC doesn't define a footer or foundation. JMHO
Ron
I agree. However, (there's always a however in life), it would make for one helluva landing for the bottom of the stairs on my deck.That is not a CEE even after the concrete is poured.
You got itdid the real CEE get missed and this is an attempt to make up for it afterwards?
Well they didn't get it.You got it
I think the rules in 250.52 are sloppy enough that you could make your own CCE separate from the building foundation and still be legal, but picture in the OP is a couple generations of thought and installation beyond that.If that is just a hole dug to contain the re-bar and concrete, and is NOT a footer or foundation, I don't believe I would accept it as a CEE.
I do understand the NEC doesn't define a footer or foundation. JMHO
Ron