interfacing the Generac nexus smart switch with different size generators

Status
Not open for further replies.
Location
Ct
When using the smart switch with a 20 kw gen set the compressor load shed and the 4 circuit priority load shed will take effect when the smart switch senses the loads climbing toward the 80 amp as not to overload the generator. How does the smart switch know if you install a 14 kw generator to it so it can shed the loads at 50 amp. Are there dip switches or programing to do to tell it?
 
When using the smart switch with a 20 kw gen set the compressor load shed and the 4 circuit priority load shed will take effect when the smart switch senses the loads climbing toward the 80 amp as not to overload the generator. How does the smart switch know if you install a 14 kw generator to it so it can shed the loads at 50 amp. Are there dip switches or programing to do to tell it?

1. By monitoring generator engine performance, the switch is able to identify when the generator approaches overload. At the appropriate time, the switch disconnects two air conditioners, typically the highest electrical load in the house.
2. After a 5-minute delay to allow for compressor bleed out, the switch brings the AC units back online one after the other with a 30-second delay in between. This is a standard capability in all Generac Smart Switches and does not require any additional components, unlike competitive transfer switches.
3. In addition, up to four other large 240V loads can be managed when the Smart Switch is used in conjunction with individual DLM modules.

  • DLM modules are 50 Amps each and are housed in a NEMA 3R enclosure, giving the installer the option to install them either at the electrical panel or anywhere in-line indoors or outdoors between the electrical panel and the appliance.
  • After the four loads are shed, they are brought back individually to assure DLM Module generator capability and eliminate the potential of overload.


a) after 3 tries or so it locks out and thats that ....
b) switch uses HZ so it does not matter what gen is hooked to it ( aircooled )
c) ther are other manufactures panels that use amps ....
 