So I am looking to get some clarity around neutral ground bonding when a main panel becomes a subpanel. Specifically if there is a new "critical load panel" which is served by a solar hybrid inverter. Lets say this critical load subpanel has a breaker that feeds an interlocked breaker in the "main panel". That way the critical panel will have automatic backup on critical loads such as, fridge, freezer, lights etc.. however in an extended grid down situation the homeowner would have the ability to swap over to the interlocked breaker in the main panel, allowing for whole home backup (within the output limits of the inverter)
My question is is this setup possible if neutral and ground are already bonded in the "main panel" where the first means of disconnect is the main breaker ? Or for this setup to be possible must the neutral ground bond occur at a first means of disconnect that is further upstream?
I have attached a quick line diagram. I am guessing that option 1 would not be okay since the main panel becomes a subpanel so it is not allowed to have the neutral ground bond. But option 2 would be okay since the neutral ground bond does not take place in the main panel but further upstream? Any thoughts on this or similiar setups would be appreciated
.
My question is is this setup possible if neutral and ground are already bonded in the "main panel" where the first means of disconnect is the main breaker ? Or for this setup to be possible must the neutral ground bond occur at a first means of disconnect that is further upstream?
I have attached a quick line diagram. I am guessing that option 1 would not be okay since the main panel becomes a subpanel so it is not allowed to have the neutral ground bond. But option 2 would be okay since the neutral ground bond does not take place in the main panel but further upstream? Any thoughts on this or similiar setups would be appreciated
.