Would you mind letting us know how much time you have in that installation by the time you're done with it?
And is your install new construction or upgrade of existing?
Thanks!
Will do, I'm doing two at the same time for the state. They will be slightly different as one is a small 6 chair dental suite and the other is 10K square of office.
OK, possible dumb question; when the label on the device and the information in the installation manual are in conflict, which prevails?
Read the post. Two different insulation temp requirements for field wiring as a specific example.
Southwire Type THHN or THWN-2* conductors are primarily used in conduit and cable trays for services, feeders, and branch circuits in commercial or industrial applications as specified in the National Electrical Code. When used as Type THHN, conductor is suitable for use in dry locations at temperatures not to exceed 90?C. When used as Type THWN-2*, conductor is suitable for use in wet or dry locations at temperatures not to exceed 90?C or not to exceed 75?C when exposed to oil or coolant. # When used as Type MTW, conductor is suitable for use in wet locations or when exposed to oil or coolant at temperatures not to exceed 60?C or dry locations at temperatures not to exceed 90?C (with ampacity limited to that for 75?C conductor temperature per NFPA 79). Conductor temperatures not to exceed 105?C in dry locations when rated AWM and used as appliance wiring material. Voltage for all applications is 600 volts.
AWM cable is intended for internal wiring of factory-assembled, listed appliances suchas computers, business machines, ranges, washers, dryers, radios, and televisions. In some cases, AWM cable may be used for external connection.
OK, possible dumb question; when the label on the device and the information in the installation manual are in conflict, which prevails?
I'm reading the install/programing instructions for an ET9000 series timer. Note the min conductor insulation temp in the chart on the bottom left of the following.
Comments?
What the heck is going on? Did everybody leave the house and you're stuck there alone? Cable went out?The plot thickens, appears 105?C is only for 30A loads.
I'd check to see if the two sources had different dates. It appears that the label is undated (date code probably about apparatus build date), so the next step would be to call the manufacturer.