I changed a friends timer guts out because it was not keeping the correct time.
The timer is for his sprinklers at his house. The voltage to the motor is 114.3 volts. The service is only 114.3 on one leg and 114.9 on the second. If I remember correctly the code used to limit the combined voltage drop to a total of 5% between the POCO and the electrician to his furthest run. I thought is was 3% for one and 2% for the other. So at the lowest shouldn't I get 116.4 at the panel?
Also, I checked the original timer and it had the hot conductor connected to the "Common" terminal. The grounded conductor to "Clock" and the load was connected to a terminal marked No. (IFIRC)
I thought that this was wrong. The motor turned in either configuration. But the switch for off/on/auto was going to "common" and the "load" (No.).
Any way the two questions are could the lower voltage be affecting the clock motor? If so could the voltage have dropped on the POCO's side recently. They have lived in this same house for about 15 years and the timer worked fine.
I have always refered to the wire from the power source as "line". The wire from the equipment being powered as "Load". The white grounded conductor as the Neutral or Common. Is that wrong.
BTW, the scematic for the clock seemed to show the load as "Line".
Here is a link to the for the clock with a link to the instructions included on that page.
http://www.intermatic.com/Default.asp?action=prod&pid=9120&sid=233&cid=51&did=5
I install Intermatic clocks all the time and they are usually marked for line, load and neutral. So this threw me for a loop...
The timer is for his sprinklers at his house. The voltage to the motor is 114.3 volts. The service is only 114.3 on one leg and 114.9 on the second. If I remember correctly the code used to limit the combined voltage drop to a total of 5% between the POCO and the electrician to his furthest run. I thought is was 3% for one and 2% for the other. So at the lowest shouldn't I get 116.4 at the panel?
Also, I checked the original timer and it had the hot conductor connected to the "Common" terminal. The grounded conductor to "Clock" and the load was connected to a terminal marked No. (IFIRC)
I thought that this was wrong. The motor turned in either configuration. But the switch for off/on/auto was going to "common" and the "load" (No.).
Any way the two questions are could the lower voltage be affecting the clock motor? If so could the voltage have dropped on the POCO's side recently. They have lived in this same house for about 15 years and the timer worked fine.
I have always refered to the wire from the power source as "line". The wire from the equipment being powered as "Load". The white grounded conductor as the Neutral or Common. Is that wrong.
BTW, the scematic for the clock seemed to show the load as "Line".
Here is a link to the for the clock with a link to the instructions included on that page.
http://www.intermatic.com/Default.asp?action=prod&pid=9120&sid=233&cid=51&did=5
I install Intermatic clocks all the time and they are usually marked for line, load and neutral. So this threw me for a loop...