One of our professional buildings is getting power glitches 3 times a week on average causing the backup generator to pick up the load. This building contains our IT dept and has servers as well as other communication equipment. As you can see in the photos, power is remaining constant, but amperage is dumping to nearly zero for a brief period. The metering device was installed at the main 800 amp switchboard on the breaker feeding the generaters transfer switch. The utility company is supplying us with 120/208Y power from a pad mounted transformer within 25 feet of the main electrical room. The utility company has checked out their transformer and informed us that the problem is not from the utility. I suspect a neutral problem somewhere or maybe the main switchgear's grounding electrode conductor has gone bad or been compromised somehow? We have loked for visual signs of problems by opening up all covers on the switchgear as well as all panels throughout the building. No obvious signs of problems. Looking for some experts here that have had similar problems! We have scheduled to have an infrared thermal scan done to the building.
Thank you