I am running a 7.5 hp 260v 3 phase pump motor using a 20hp vfd with single phase 260v input. (the location does not have 3 phase power available) The unit has run without problems for several years until 3 months ago when I started having trouble with the 100 amp main breaker tripping. The first time it happened, I took off the inspection plate on the motor and noted that one of the leads was showing signs of overheating, so I re-terminated it, checked the motor for shorts to ground, there weren't any.
I assumed that the connection at the lead had either heated up from resistance or grounded out inside the terminal box. So I powered it back up and things worked well for another month or so. Then I came back one day, and noted that one of the slow-blow 60 amp fuses had blown, and there was damage to the disconnect between the vfd and the subpanel. Again I looked for signs of overheating, shorts, etc. and found no concerning signs. So I connected the VFD directly to the 50 amp subpanel breaker.
This was the beginning of the current (not a pun) problem: The motor runs for 1-2 hours, then trips either the 100amp main or the 50 amp subpanel breaker. Each time, the VFD will show a fault on the either "DC bus low voltage" , or more often: "Line Loss." I have tested the motor insulation and each phase to ground is uniformly 55M ohm for a 5 minute 500v test. I am concerned that the motor may be at fault as it is not an inverter grade motor. It is an f grade of insulation, which when I spoke to a motor tech at Baldor said it would be worth trying to see how well it works.
I'm having a hard time figuring out what I need to correct. There is a very significant short going on, sufficient to trip the circuit breaker, but it does not persist. When I reset the breaker, the motor runs again for another hour. I have checked the voltages and amperages of the 3 phases, and the 3 legs show close to equal amperages ( +/- 15 amps)lamp-on, as do the 2 legs of the single phase (+/- 25 amps). Suggestions on where to go from here in correcting this problem?
I assumed that the connection at the lead had either heated up from resistance or grounded out inside the terminal box. So I powered it back up and things worked well for another month or so. Then I came back one day, and noted that one of the slow-blow 60 amp fuses had blown, and there was damage to the disconnect between the vfd and the subpanel. Again I looked for signs of overheating, shorts, etc. and found no concerning signs. So I connected the VFD directly to the 50 amp subpanel breaker.
This was the beginning of the current (not a pun) problem: The motor runs for 1-2 hours, then trips either the 100amp main or the 50 amp subpanel breaker. Each time, the VFD will show a fault on the either "DC bus low voltage" , or more often: "Line Loss." I have tested the motor insulation and each phase to ground is uniformly 55M ohm for a 5 minute 500v test. I am concerned that the motor may be at fault as it is not an inverter grade motor. It is an f grade of insulation, which when I spoke to a motor tech at Baldor said it would be worth trying to see how well it works.
I'm having a hard time figuring out what I need to correct. There is a very significant short going on, sufficient to trip the circuit breaker, but it does not persist. When I reset the breaker, the motor runs again for another hour. I have checked the voltages and amperages of the 3 phases, and the 3 legs show close to equal amperages ( +/- 15 amps)lamp-on, as do the 2 legs of the single phase (+/- 25 amps). Suggestions on where to go from here in correcting this problem?