figured i'd ask around just to see if there's anything i may have missed . . .
we've had a customer call twice in the past two months about an intermittent circuit breaker tripping.
the circuit includes the refrigerator, a sunroom (receps and lighting), and some hallway lighting.
on the first visit the customer indicated the breaker had tripped at some point during the night for 5 consecutive days before we came out.
i went out and checked the current on the offending circuit and found under normal use it was pulling 3A; this is the fridge and a few lights. Startup current on compressor was 14A (checked w/ min/max). VD = 2% under full load.
i checked all device terminations; everything looked good. circuit resistance was fine also. I also checked every light bulb on all the fixtures in the circuit as i've seen blowing bulbs trip a breaker; they were all working fine.
told them it had to be something in the fridge.
they called again last week except this time said they breaker wouldn't reset.
customer indicated the breaker tripped and after several attempts to reset, they ran an extension cord to the fridge. they had not touched the breaker since.
the customer did not attempt a reset w/ the fridge unplugged. i did, and it work. ran my battery of tests again and everything came out fine.
i checked the compressor for ground leaks and found none, and the relay didn't show any signs of overheating. i'm not an appliance guy so that's as far as i could go with it.
in my opinion there is no problem w/ the premises wiring, but can anyone think of something i overlooked?
we've had a customer call twice in the past two months about an intermittent circuit breaker tripping.
the circuit includes the refrigerator, a sunroom (receps and lighting), and some hallway lighting.
on the first visit the customer indicated the breaker had tripped at some point during the night for 5 consecutive days before we came out.
i went out and checked the current on the offending circuit and found under normal use it was pulling 3A; this is the fridge and a few lights. Startup current on compressor was 14A (checked w/ min/max). VD = 2% under full load.
i checked all device terminations; everything looked good. circuit resistance was fine also. I also checked every light bulb on all the fixtures in the circuit as i've seen blowing bulbs trip a breaker; they were all working fine.
told them it had to be something in the fridge.
they called again last week except this time said they breaker wouldn't reset.
customer indicated the breaker tripped and after several attempts to reset, they ran an extension cord to the fridge. they had not touched the breaker since.
the customer did not attempt a reset w/ the fridge unplugged. i did, and it work. ran my battery of tests again and everything came out fine.
i checked the compressor for ground leaks and found none, and the relay didn't show any signs of overheating. i'm not an appliance guy so that's as far as i could go with it.
in my opinion there is no problem w/ the premises wiring, but can anyone think of something i overlooked?