eag
- Huntsville, AL
Background - 3-phase, 2000A service fed from 3 single-phase pole mounted transformers. Switchgear is NEMA-3R, manufacturer unknown (may be GE), with push-to-trip, handle-actuated draw-in mechanism, with 1600A fuses.
Problem - There is loss-of-phase occuring intermittently (anywhere from 3-7 days apart recently) on the C phase. Analysis so far shows that voltage downstream from the main is normal up to to point of phase loss, then upon loss-of-phase falls to between 0-10V for anywhere between 30 minutes to an hour before returning back to normal voltage. What could cause this sort of intermittent loss-of-phase in the system described?