TwoBlocked
Senior Member
- Location
- Bradford County, PA
- Occupation
- Industrial Electrician
Usually, but not always, I can point to a bad resistance between terminals or a bad megger resistance to ground to say a motor is bad. Today was not one of those times. It was a vibrator 480V 3-ph with 3 FLA, WYE configuration. It was tripping OL, drawing 25 amps an each of the three legs. Took the covers off and it spun freely by hand. OK, measuring from the top of the contactor with the contacts pushed in it's not an open, ground, or mechanical binding, nor an obvious short. That leave an internal fault. I was expecting to see a current imbalance between the legs. That points to one of the coils in this wye motor, but they all read the same. That leaves the stator and the rotor. That also leaves me behind...
So motor gurus: what sort of fault might cause high current in a motor that passes ordinary test?
So motor gurus: what sort of fault might cause high current in a motor that passes ordinary test?