Greetings all, we have a project involving re-feeding a large sign like you typically see for a gas station along the highway.
The sign contractor requested 3 120V circuits for the internal lights and displays in the sign, 2X30's and a 20, flown overhead.
If a sign is a 'structure' per 225.30 I cant see how it would be legal to feed a sign with more than one branch circuit or feeder.
I could just use a 60A feeder and tap rules, but that would lead to OCPD's inside the sign way up in the top upper section.
It seems like 240.10 may allow these OCPD's to be inside the sign if there is a disconnect within sight of the sign on the building that feeds it per 600.6(A)(2)?
600.6(A)(1) Exception No 2 mentions "internal panelboards" in a sign.
Is this something that is commonly done?
We usually do signs with a underground feeder and have a lockable panel near or at the base of the sign,
So this request is odd to me.
Thanks in advance .
The sign contractor requested 3 120V circuits for the internal lights and displays in the sign, 2X30's and a 20, flown overhead.
If a sign is a 'structure' per 225.30 I cant see how it would be legal to feed a sign with more than one branch circuit or feeder.
I could just use a 60A feeder and tap rules, but that would lead to OCPD's inside the sign way up in the top upper section.
It seems like 240.10 may allow these OCPD's to be inside the sign if there is a disconnect within sight of the sign on the building that feeds it per 600.6(A)(2)?
600.6(A)(1) Exception No 2 mentions "internal panelboards" in a sign.
Is this something that is commonly done?
We usually do signs with a underground feeder and have a lockable panel near or at the base of the sign,
So this request is odd to me.
Thanks in advance .