What is meant by the internal power factor of a transformer or internal pf of a synchronous generator
Never heard the term of power factor as used with a transformer. Transformers are rated in Kva. Simply put, the max amperage that can run through it at a given voltage. Increase the PF of the load and get more capacity out of the transformer.
I have actual test data on a 400kVA unit.141111-2114 EST
A particular 175 VA 120 V primary unloaded transformer with with 123 V input has a PF = 0.21 .
A surprising result I had not expected. At 100 V the PF increased to 0.25, and at 130 V PF dropped to 0.16 .
Is Kill-A-Watt EZ giving me bad readings? Probably not. With a load of 30 mfd shunted with 460 ohms the EZ PF reading remained at 0.18 from 100 V to 130 V.
Why the transformer has the above characteristic will have to wait for some future analysis.
.
A transformer at no load is a rich source of harmonics. So testing with a harmonic analyser rather than Kill-A-Watt EZ would give a clue to the riddle.141111-2114 EST
A particular 175 VA 120 V primary unloaded transformer with with 123 V input has a PF = 0.21 .
A surprising result I had not expected. At 100 V the PF increased to 0.25, and at 130 V PF dropped to 0.16 .
Is Kill-A-Watt EZ giving me bad readings? Probably not. With a load of 30 mfd shunted with 460 ohms the EZ PF reading remained at 0.18 from 100 V to 130 V.
Why the transformer has the above characteristic will have to wait for some future analysis.
.