by 'continuous length' does this mean no splices?
thnx
(5) Be of continuous length. Where 501.140(A)(5) is applied,
cords shall be of continuous length from the power
source to the temporary portable assembly and from the
temporary portable assembly to the utilization equipment.
That would seem to be the case. I wonder why they added the word length in there.
You may wish to consider Section 90.3 which states Chapter 5 supplements or modifies the general rules of Chapters 1-4.
Also note Section 501.140 applies to both Division 1 and 2 without distinction. "General" splices are considered arc-making, especially in high vibration conditions where they may loosen without special precautions.
Ingress into cables at terminals is covered in the first sentence of Section 501.15(D)(1) for Division 1. Division 2 is a little different since there isn't supposed to be any gases in the first place and only enclosures required to be explosionproof are covered that way. In any case, Section 501.140 (B)(3) requires terminations for covered cables to be made such that there is no stress on the terminations.I am meeting with our solicitor tomorrow
he thinks since both sections ref continuous, but the splicing portion is omitted from 501, that is intentional, and de facto splicing is not allowed
arcing is one concern
the other is ingress of gas thru the cable into an enclosure
do you have a ref for general splices are considered arc producing?
I have a fairly good idea how explosionproof enclosures work. Explosionproof enclosures leak through every threaded penetration - period; especially with methane. Leaking through the cable interstices is actually pretty trivial if the cable is sealed properly per Section 501.15(E).
If you’re monitoring your air-flow properly, gas detectors are pretty much a waste.
If you’re concerned about coal you might want to consider Section 502.5 as well with regard to explosionproof enclosures. It’s also Class II, Group F.
Is it State law or MSHA that’s requiring NEC compliance?
I suspect the original purpose of the gas detection system was/is more for toxicity than fire protection. Save the canaries. There are however some fairly rigorous requirements for applying combustible gas detection systems in Section 500.7(L). I suspect you are already meeting them.
Depending on the NEC edition in place, you may want to review Sections 501.15 (E)(3)&(4) as well. Not so much for boundary conditions in your case, but the opinion/philosophy of the CMP with regard to gases entering the cable at locations other than the terminations. Avoid the 2014 edition if you can, you will arrive at the same conclusions but it’s much more difficult to decipher. Except for type MI, no cable construction currently meets the requirements of Section 501.15(E)(2) although it does indicate the requirements for an adequate seal.
”May” is indeed the operative term for Class I, Division 2.