The 2011 NEC revised article 338 in a way that I am having a hard time understanding and AHJs seem to be having as well. I am looking at this from the multifamily point of view where each unit is fed with an SE type of cable from the meter locations to the load centers and that cable is in touch with insulation for most of the run. I am referring to the second paragraph of 338.10(B)(4)(a). This new requirement of using the 60 deg column when installed in insulation is becoming a bit confusing. Here are the main points of concern:
1 - The phrase "installed in thermal insulation" has been interpreted thus far in two different ways: some argue that insulation on one side only would not apply and some argue that in touch with insulation is enough for the rule to kick in.
2 - If an apartment is fed with 120/240 we can go by table 310.15(B)(7) and let's say a 125 Amp service would be fed by a 1/0 AL SE cable (regardless of insulation being present or not according to informational note 2 of article 338.10(B)(4)(a)). If the same apartment is fed with 120/208 we have to go by table 310.15(B)(16) as usual but now in presence of insulation we might have to upgrade to the 60 degree column so the 125 Amp service would need a 3/0 AL SE cable. I cannot make sense of the same amps traveling in the conductors yet one having to use a 3/0 cable whereas the other one is ok with a 1/0 cable (with the same type of cable installed under the same circumstances). Furthermore, most manufacturers limit the typical tenant breakers to accept up to 2/0 conductors so we would need to increase the size of the breakers and the meter stacks to accommodate this under 120/208 but not under 120/240.
So far I have consulted a manufacturer, an engineer, and two AHJs, not two answers have been the same. Has anyone come across it?
1 - The phrase "installed in thermal insulation" has been interpreted thus far in two different ways: some argue that insulation on one side only would not apply and some argue that in touch with insulation is enough for the rule to kick in.
2 - If an apartment is fed with 120/240 we can go by table 310.15(B)(7) and let's say a 125 Amp service would be fed by a 1/0 AL SE cable (regardless of insulation being present or not according to informational note 2 of article 338.10(B)(4)(a)). If the same apartment is fed with 120/208 we have to go by table 310.15(B)(16) as usual but now in presence of insulation we might have to upgrade to the 60 degree column so the 125 Amp service would need a 3/0 AL SE cable. I cannot make sense of the same amps traveling in the conductors yet one having to use a 3/0 cable whereas the other one is ok with a 1/0 cable (with the same type of cable installed under the same circumstances). Furthermore, most manufacturers limit the typical tenant breakers to accept up to 2/0 conductors so we would need to increase the size of the breakers and the meter stacks to accommodate this under 120/208 but not under 120/240.
So far I have consulted a manufacturer, an engineer, and two AHJs, not two answers have been the same. Has anyone come across it?