Interpretation of NEC 220.83
Tainted
New York
Engineer (PE)
NEC 220.83 says this:
This section shall be permitted to be used to
determine if the existing service or feeder is of
sufficient capacity to serve additional loads. Where the dwelling
unit is served by a 120/240-volt or 208Y/120-volt, 3-wire service,
it shall be permissible to calculate the total load in accordance
with 220.83(A) or (B).
Can this be used to calculate your new service if the existing service is insufficient? The way I'm interpreting it is that it tells you it should be used to only check if the service is sufficient, nothing more. It doesn't tell you it should be used for calculating your new service if the service is insufficient.
This is not used for a new service. It is only used to determine if the existing service can new loads being added to an existing service.
f this tells you the existing service is not adequate for adding additional loads, you would do a complete service calculation covering both the existing and new loads to determine the size of a new service.