buzzbar
Senior Member
- Location
- Olympia, WA
- Occupation
- Electrical Contractor
Hi all,
I know that this has been discussed many times, but I haven't found an answer that matches my exact situation.
Here's the deal: I'm working on a marina that is in the process of upgrading in phases. There are five (5) docks (salt water) that are fed from an existing 480V main distribution panel. Currently, there is a 3P150A breaker for each dock that feeds a transformer that is located on the floating docks.
Phase 1 is replacing docks 4 and 5. The feeder for dock #4 will be increased from 150A to 225A, so we will be altering (replacing) the existing feeder. Since both docks will be replaced with new wiring, it needs to be brought up to the latest code, which in Article 555.3, it says:
555.3 Ground-Fault Protection. The main overcurrentprotective device that feeds the marina shall have groundfault protection not exceeding 100 mA. Ground-fault protection of each individual branch or feeder circuit shall bepermitted as a suitable alternative.
Each new dock will again, have a transformer on the floating dock that will step down from 480V to 120/208V (don't get side-tracked by the 208V, I'm aware of the FPN about that).
My local AHJ says that the main 480V feeder coming from shore to the transformer needs to have ground fault protection (GFP). I would argue that 555.3 allows for the GFP to be located on the main breaker of the secondary panel (or at each sub-feeder for pedestals) since 555.3 says, "Ground-fault protection of each individual branch OR feeder circuit shall be permitted as a suitable ALTERNATIVE".
Talking to my Eaton rep, he says that they don't normally GFP the primary side of the transformers, but they can certainly build them that way.
At the very least, it's a very vague couple of sentences, and should be cleared up.
Thoughts?
Thanks!
Andy
I know that this has been discussed many times, but I haven't found an answer that matches my exact situation.
Here's the deal: I'm working on a marina that is in the process of upgrading in phases. There are five (5) docks (salt water) that are fed from an existing 480V main distribution panel. Currently, there is a 3P150A breaker for each dock that feeds a transformer that is located on the floating docks.
Phase 1 is replacing docks 4 and 5. The feeder for dock #4 will be increased from 150A to 225A, so we will be altering (replacing) the existing feeder. Since both docks will be replaced with new wiring, it needs to be brought up to the latest code, which in Article 555.3, it says:
555.3 Ground-Fault Protection. The main overcurrentprotective device that feeds the marina shall have groundfault protection not exceeding 100 mA. Ground-fault protection of each individual branch or feeder circuit shall bepermitted as a suitable alternative.
Each new dock will again, have a transformer on the floating dock that will step down from 480V to 120/208V (don't get side-tracked by the 208V, I'm aware of the FPN about that).
My local AHJ says that the main 480V feeder coming from shore to the transformer needs to have ground fault protection (GFP). I would argue that 555.3 allows for the GFP to be located on the main breaker of the secondary panel (or at each sub-feeder for pedestals) since 555.3 says, "Ground-fault protection of each individual branch OR feeder circuit shall be permitted as a suitable ALTERNATIVE".
Talking to my Eaton rep, he says that they don't normally GFP the primary side of the transformers, but they can certainly build them that way.
At the very least, it's a very vague couple of sentences, and should be cleared up.
Thoughts?
Thanks!
Andy