dnatoy
Member
- Location
- United States
We have installation in a single room with high voltage (480/277V) and low voltage (208/120V) panels located next to each other on same wall. Transformer is located above 2'x4' grid ceiling with removable acoustic tiles in the same room. Transformer is fed from circuit breaker located in the high voltage panel. Low voltage panel has main circuit breaker. Feeder from transformer to panel is less than 10 feet long. OCPD's are sized per NEC requirements. We were enforced by local building electrical inspector to install disconnect switch on the primary side of the transformer, because "when somebody works with transformer above the ceiling grid, this person cannot see high voltage panel and transformer's circuit breaker." We provided this modification, but it seems overkill on building department's side. What is you thought about it?