ceknight
My current installation failed inspection today, despite being well up to what I (and previous inspectors) thought was a correct interpretation of NEC 250.64 (C). ("Grounding electrode conductor(s) shall be installed in one continuous length without a splice or joint except as permitted...." etc).
I interpret that to mean the GEC must be continuous from the grounding busbar all the way to its terminus at the 2nd electrode. No prob, that's how I've always done it, and it always passed.
Today's inspector claims that NEC 250.64(C) requires the GEC to originate at the busbar, travel continuously to clamps at both electrodes, then return to the panel and terminate at the busbar. So the GEC forms a loop from the panel to the electrodes and back to the panel.
Does anyone else interpret the rule that way he did, and if so, is one interpretation to be favored over the other?
Any help is appreciated.
Thanks,
Chris Knight
(Moderator?s Note: Edited to remove email address. If you wish to send an email message to this person, then first send a Private Message via this Forum, and ask for the email address.)
Syracuse NY
[ January 31, 2006, 05:24 PM: Message edited by: charlie b ]
Thanks,
Chris Knight
Syracuse NY