I?ve already read many of the posts about NEMA 12 enclosures on this forum and have learned a lot of good info. Thank you! :thumbsup:
My old (and limited) understanding of a NEMA 12 enclosure was that it was for oily environments and that the enclosure was essentially liquid tight. With the popularity of VFDs and the need to deal with their heat output I have seen enclosures claiming to be NEMA 12 with open vents protected only by a coarse see through material. Others have had vents with paper filters similar to furnace filters. Neither seems ideal for an oily environment and by my old understanding would not be acceptable as a type 12 enclosure.
After reading the current ?degree of protection? language I do not know how one can decide when something meets the intent of the rating, specifically NEMA Type 12. A manufacturer or panel builder can claim the coarse foam will offer a ?degree of protection? against light splashing, but imo that is really pushing it.
What say the experts on this subject, how/where does one draw the line between what is true type 12 and what is not?
My old (and limited) understanding of a NEMA 12 enclosure was that it was for oily environments and that the enclosure was essentially liquid tight. With the popularity of VFDs and the need to deal with their heat output I have seen enclosures claiming to be NEMA 12 with open vents protected only by a coarse see through material. Others have had vents with paper filters similar to furnace filters. Neither seems ideal for an oily environment and by my old understanding would not be acceptable as a type 12 enclosure.
After reading the current ?degree of protection? language I do not know how one can decide when something meets the intent of the rating, specifically NEMA Type 12. A manufacturer or panel builder can claim the coarse foam will offer a ?degree of protection? against light splashing, but imo that is really pushing it.
What say the experts on this subject, how/where does one draw the line between what is true type 12 and what is not?