When it comes to interpreting 250.122(B), when you increase parallel conductors to account for voltage drop, is the calculation for increasing the grounding conductor based on an "apples to apples" quantity comparison of the ungrounded conductors, or just the amperage capacity of the ungrounded conductor?
For example:
An 800A feeder is upsized for voltage drop from (2) sets of 600KCMIL to (3) sets of 600KCMIL.
Example #1: Using (3) sets (apples to apples) of 300KCMIL, (855A)-grounding conductor increases by 200% from #1/0 to #4/0
Example #2: Using (2) sets of 600KCMIL, (840A)-grounding conductor increases by 150% from #1/0 to #3/0
In this scenario, the resulting grounding conductor is only 1 conductor size difference but depending on the feeders, there could be quite a difference in the conductor size.
What would be the correct way to calculate this, or is it subject to interpretation?
Thanks in advance!