malachi constant
Senior Member
- Location
- Minneapolis
Hi all,
I'm a licensed engineer, trying to make sense of a thermography report dropped on my desk. It is a new installation (standard 480V & 208V breaker panels and transformers). Owner asked the contractor to provide infrared scans of the equipment to look for potential issues. I'm not sure how to read these.
* Are there certain rise-over-ambient temperatures that are red flags? (Not sure where to get ambient from the data, but I am assuming it is roughly 72F.)
* Panels: The images draw your eyes to the hot spots, but then when you look over to the scale you see the white hot "hot spot" is only 82F, so no big deal, right? What if this 82F hot spot is three phase wires coming out of a breaker, and they stay "hot" all the way out of the panel?
* Out of the 100 or so panels I only see a couple that have any spots over 90F, and only one that approaches 100F. The 100F probably merits attention - in a 100A 208V panel, looks like it is at a neutral or ground bar (though they didn't provide a visible light photo of that equipment so I can't see very clearly what I'm looking at).
* Transformer connections look good, but a bar of some sort near the top of the transformers is frequently up in the 130-150F range. I'm assuming this is not an issue as it appears in nearly every transformer.
* Motor disconnects: most look fine, but on a makeup air disconnect there's a component of some sort that is pushing 170F. A compressor disconnect hits 145F.
Normally I can learn a skill like this by doing some research online, but haven't found the right links that break down the images and state what is advisory vs serious vs critical. I'm sure it is somewhat of an art, but also suspect with a few pointers as a licensed engineer I should be able to read these with a degree of confidence. Any help is appreciated!
I'm a licensed engineer, trying to make sense of a thermography report dropped on my desk. It is a new installation (standard 480V & 208V breaker panels and transformers). Owner asked the contractor to provide infrared scans of the equipment to look for potential issues. I'm not sure how to read these.
* Are there certain rise-over-ambient temperatures that are red flags? (Not sure where to get ambient from the data, but I am assuming it is roughly 72F.)
* Panels: The images draw your eyes to the hot spots, but then when you look over to the scale you see the white hot "hot spot" is only 82F, so no big deal, right? What if this 82F hot spot is three phase wires coming out of a breaker, and they stay "hot" all the way out of the panel?
* Out of the 100 or so panels I only see a couple that have any spots over 90F, and only one that approaches 100F. The 100F probably merits attention - in a 100A 208V panel, looks like it is at a neutral or ground bar (though they didn't provide a visible light photo of that equipment so I can't see very clearly what I'm looking at).
* Transformer connections look good, but a bar of some sort near the top of the transformers is frequently up in the 130-150F range. I'm assuming this is not an issue as it appears in nearly every transformer.
* Motor disconnects: most look fine, but on a makeup air disconnect there's a component of some sort that is pushing 170F. A compressor disconnect hits 145F.
Normally I can learn a skill like this by doing some research online, but haven't found the right links that break down the images and state what is advisory vs serious vs critical. I'm sure it is somewhat of an art, but also suspect with a few pointers as a licensed engineer I should be able to read these with a degree of confidence. Any help is appreciated!