I understand that SCCR and IR are not the same thing. Fuses and Circuit breakers have IR's, and contactors and other power components have SCCR's. The SCCR of an entire equipment cannot be greater than the lowest IR or the lowest SCCR. The SCCR for the equipment is typically the lowest SCCR or IR of the power components.
With that being said, is there any benifit in knowing the IR of a machine if you already know the SCCR? I think it i would just be confusing to list both on a single machine. Someone may look at a machine and think "Wow, it has an IR of 25KA", but the SCCR is only 5KA.
I know there is a requirement to put the SCCR on equipment labeling, but is there also a requirement to put the IR on the label? Was the IR on the label before the SCCR labeling requirement came into affect several code cycles ago?