I am trying my hand at estimating max available fault current at a GE 480VAC panel (with several TEY CBs (60A, 30A, 100A)). I will try to describe this situation.
The incoming service transformer is a 12.47KV prim, 480VAC primary, 2500KVA, 5.52%Z. This service transformer secondary is feeding a GE spectra series switchboard with a 4000A main. The feed from the transformer to the main is approximately 55', 12 conductor per phase, 600mcm per conductor. From the switchboard, we use a 400A CB to feed a 480VAC panel. This panel has several GE TEY breakers all of which is rated for 14KA interrupting current. The cable length from the 400A CB to the 480VAC panel is approximately 277'. We ran 2 conductors per phase of 3/0 cu THHN. Given the maximum primary fault current (3.41primary), I computed the max available short circuit current at the 480VAC panel to be around 14.2KA not included the motor contribution downstream of this panel.
My question is if this number is correct (i.e 14.2KA) and the CBs in this panelboard is only rated for 14KA, is this an issue? I tried to get a better measurement for cable length but the number just does not work out. By the way, the cable is rated for 40C ambient and 90C for conductor. Is there an issue with my calculations? There are 6 other panels that are about the same distance and conductors and their fault currents are all a little larger than 14.2KA.
Thank you in advance.
Francis.
I am trying my hand at estimating max available fault current at a GE 480VAC panel (with several TEY CBs (60A, 30A, 100A)). I will try to describe this situation.
The incoming service transformer is a 12.47KV prim, 480VAC primary, 2500KVA, 5.52%Z. This service transformer secondary is feeding a GE spectra series switchboard with a 4000A main. The feed from the transformer to the main is approximately 55', 12 conductor per phase, 600mcm per conductor. From the switchboard, we use a 400A CB to feed a 480VAC panel. This panel has several GE TEY breakers all of which is rated for 14KA interrupting current. The cable length from the 400A CB to the 480VAC panel is approximately 277'. We ran 2 conductors per phase of 3/0 cu THHN. Given the maximum primary fault current (3.41primary), I computed the max available short circuit current at the 480VAC panel to be around 14.2KA not included the motor contribution downstream of this panel.
My question is if this number is correct (i.e 14.2KA) and the CBs in this panelboard is only rated for 14KA, is this an issue? I tried to get a better measurement for cable length but the number just does not work out. By the way, the cable is rated for 40C ambient and 90C for conductor. Is there an issue with my calculations? There are 6 other panels that are about the same distance and conductors and their fault currents are all a little larger than 14.2KA.
Thank you in advance.