FORK said:I am getting a price quote on 600amp 480volt I-line main. My supplier needs to know what interrupting rating I need, 10k...22k & so on. I'm drawing a complete blank on calculating what I need. Any thoughts?
kingpb said:Keeping that in mind, the utility could provide a smaller transformer, and often times they do. Which means you might be able to use lower impedance and still be under the 22KAIC. However, this is risky, because they could also come and change the transformer later, and then you might have a problem.