I have a phone board on the second level and the intersystem bonding is located in down stairs electrical room. Can I take my #6 to building steel. Or does have to go back to intersystem per 800. There is a education. In 250.94

Sent from my SM-G950U using Tapatalk
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
800.100(B)(1) doesn’t seem to leave wiggle room. It shall be connected to the IBT.

They included a new option in 250.94(B), but neglected to instruct us to connect it to anything as required in (A). :slaphead:

The exception to (A) would be for buildings existent prior to the IBT requirement.
 

Sahib

Senior Member
Location
India
The code intent, IMO, is to avoid two ground references at the phone board: one from connecting #6 to building steel ground and other possibly from coaxial cable shield connected to some other ground.
 