504.30(A)(1)
Exception No. 2: Where either (1) all of the intrinsically
safe circuit conductors or (2) all of the nonintrinsically safe
circuit conductors are in grounded metal-sheathed or
metal-clad cables where the sheathing or cladding is capable
of carrying fault current to ground.
I would like to run the intrinsic circuits in a shielded cable. If my power cable is fed from 60a OCPD would the shield on the intrinsic cable have to be rated for 60a?
Exception No. 2: Where either (1) all of the intrinsically
safe circuit conductors or (2) all of the nonintrinsically safe
circuit conductors are in grounded metal-sheathed or
metal-clad cables where the sheathing or cladding is capable
of carrying fault current to ground.
I would like to run the intrinsic circuits in a shielded cable. If my power cable is fed from 60a OCPD would the shield on the intrinsic cable have to be rated for 60a?