I have been scouring the latest National Electric Code as well as the internet and am unclear of the answer to this question and hope that the people of this form can help. I am looking for chapter and verse from the National Electrical Code or any code standard.
If you follow article 501.10 (a) of the National Electric Code for Class 1 Division 1 conduit, seals, and wiring, and if your instrumentation meets the requirements of article 501.105 (a).
Are you required to add an intrinsically safe barrier, say from a PLC panel that is in an unclassified area to say a pressure transmitter that is in a class 1 div 1 area and is rated for a class 1 div 1 area along with all the conduit and wire properly installed?
I am struggling to find the answer and hoping you all could help.
I do understand that if the customer requires a barrier, you add one, but I’m more interested if the customer is silent on the matter.