cdcabrera
Member
- Location
- Riverside, CA
Got a new installation for hydrogen service and the customer wants it to be IS. Skid mounted oil separation unit, all device wiring will be pulled a JB on the edge of the skid. Customer is responsible for wiring back to the control system.
Based on my research I understand the following items
- any wiring method is acceptable
- wiring needs to be blue in color
- cabling/cable trays need to be clearly/permanently identified "Intrinsically Safe" at min every 7.5m or 25ft
- in the event there is wiring that is not IS, it needs to be separate from the IS by 2" min
Anything else I should be considering?
Based on my research I understand the following items
- any wiring method is acceptable
- wiring needs to be blue in color
- cabling/cable trays need to be clearly/permanently identified "Intrinsically Safe" at min every 7.5m or 25ft
- in the event there is wiring that is not IS, it needs to be separate from the IS by 2" min
Anything else I should be considering?