barrydmi

Member
Location
Washington
Recently an inspector required the 120 volt circuit to a intrinsically safe relay, to be GFCI protected. He said because the relay isn't UL listed. Can anyone explain this resoning. Thanks for the help.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: Intrinsically safe relays

Possibly may be a requirement in the UL listing for IS systems, there is a UL standard 1394 or similar. Use of a GFCI is allowed in UL 508 Industrial Motor Control Standard for non listed equipment.
 